Noisy hot water mixing valve

Tue Aug 14, 2012 8:06 am

Do we have any plumbing types on TR?

On top of my gas water heater I have a Watts 1170-C thermostatic mixing valve to moderate the hot water temperature down. Unfortunately every time a tap is shut off it makes a "chunk-chink" sound - I suspect it is the mixing piston being driven across by the pressure spike. My water pressure isn't excessive, measured with a cheap gauge from Home Depot at about 75psi, and I've put water hammer arrestors on the washing machine outlets (the worst offender) but everything still causes it to make the noise. I know it is the valve and not just loose pipes because I listened to it carefully whilst my wife turned a tap on and off and also if I shut off the cold supply to the tank and mixing valve then it stops happening.

Is this just the valve going bad and I need to replace it? Or is this to be expected on this valve type? Worth trying a different manufacturer? Am I missing some pressure handling stuff in my plumbing setup to reduce the spikes or balance it across the hot and cold lines feeding in to the valve?
 
Aranarth
Graphmaster Gerbil
Posts: 1435
Joined: Tue Jan 17, 2006 6:56 am
Location: Big Rapids, Mich. (Est Time Zone)
Contact:

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 7:55 am

I would try over here:
http://www.dslreports.com/forum/homerepair

There seem to be some geeky electricians and plumbers who frequent the forum...
Main machine: Core I7 -2600K @ 4.0Ghz / 16 gig ram / Radeon RX 580 8gb / 500gb toshiba ssd / 5tb hd
Old machine: Core 2 quad Q6600 @ 3ghz / 8 gig ram / Radeon 7870 / 240 gb PNY ssd / 1tb HD
 
tanker27
Gerbil Khan
Posts: 9444
Joined: Tue Feb 26, 2002 7:00 pm
Location: Georgia

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 9:16 am

notfred wrote:
water hammer arrestors


Sorry to thread jack but I never knew this was even such a thing. So my washing machine experiences this hammer/jolt when the hot water is turned on and off or goes from hot to cold. The question I have is where does this device sit? Does it sit between the valve outlet and the hose or do you have to weld it on the pipe itself?
(\_/)
(O.o)
(''')(''')
Watch out for evil Terra-Tron; He Does not like you!
 
notfred
Maximum Gerbil
Topic Author
Posts: 4610
Joined: Tue Aug 10, 2004 10:10 am
Location: Ottawa, Canada

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 10:09 am

http://www.homehardware.ca/en/rec/index ... r+arrestor

Screw this on to the washing machine pipes at the wall, then connect the washing machine hoses to the outlet of this. There are other types that you put on the plumbing as you build the house, see the related products on the above page.
 
XorCist
Gerbil First Class
Posts: 116
Joined: Wed Apr 18, 2007 6:54 pm
Location: Clovis, CA

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 10:18 am

why do u need a hot water temp regulator coming off the water heater? why not just turn down the thermostat on the water heater itself?
 
Captain Ned
Global Moderator
Posts: 28704
Joined: Wed Jan 16, 2002 7:00 pm
Location: Vermont, USA

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 10:25 am

XorCist wrote:
why do u need a hot water temp regulator coming off the water heater? why not just turn down the thermostat on the water heater itself?

Many local plumbing codes call for the heater to be kept above 140F to kill off any nasties that might be in the water. Since 140+ is unsafe at the tap, the code also requires a mixing valve to reduce the output to 120F or lower.

I installed my own water heater so I never bothered with the mixing valve.
What we have today is way too much pluribus and not enough unum.
 
liquidsquid
Minister of Gerbil Affairs
Posts: 2661
Joined: Wed May 29, 2002 10:49 am
Location: New York
Contact:

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 10:29 am

You can make your own "Water hammer" effect remover by simply placing a 'T' somewhere along the pipe that sits upwards with a cap on the end that can hold air, and even better if you can inject air as needed. Commercial ones contain a bladder to prevent the air from dissolving away for low maintenance. The air acts as a shock-absorber. The closer to the "load", the better it will work at eliminating the vibrations.
 
XorCist
Gerbil First Class
Posts: 116
Joined: Wed Apr 18, 2007 6:54 pm
Location: Clovis, CA

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 10:37 am

Captain Ned wrote:
XorCist wrote:
why do u need a hot water temp regulator coming off the water heater? why not just turn down the thermostat on the water heater itself?

Many local plumbing codes call for the heater to be kept above 140F to kill off any nasties that might be in the water. Since 140+ is unsafe at the tap, the code also requires a mixing valve to reduce the output to 120F or lower.

I installed my own water heater so I never bothered with the mixing valve.


ahh the joys of living in california...good luck getting a water heater to go over 140..LOL so many failsafes its stupid...never knew of a code like that...knowledge is power...

anywho i was doing some googling and found this http://www.plumbersurplus.com/pdf/01741.pdf down on the second page has this
Valve is noisy • Water velocity is too high• Reduce water velocity with pressure regulating valves

so i'd assume ur running 3/4" to it, you could try http://www.homedepot.com/webapp/wcs/sto ... CvBUJZFk6I it outputs at 50psi, so that should help you.
 
Captain Ned
Global Moderator
Posts: 28704
Joined: Wed Jan 16, 2002 7:00 pm
Location: Vermont, USA

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 11:44 am

notfred:

Put an expansion tank on the cold water supply line. Should fix your problems right quick. An expansion tank will also solve any problems with a weepy/drippy T&P relief valve.
What we have today is way too much pluribus and not enough unum.
 
notfred
Maximum Gerbil
Topic Author
Posts: 4610
Joined: Tue Aug 10, 2004 10:10 am
Location: Ottawa, Canada

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 12:44 pm

liquidsquid - Without a way to inject air e.g. by draining down the system, all the air will be gone in a year or so. The ones I linked to are the commercial variety.

XorCist - The valve noise they are talking about in the PDF is flow noise, usually a whistling noise. I'm getting noise with no flow through the valve. I was looking at just that pressure regulator when I thought my pressure was excessive and the noise was plain water hammer, but 80psi is right on the upper end of the normal range from my reading, so I'm not sure a pressure reducing valve will help.

Captain Ned - I don't have any backflow prevention on the cold water feed that I am aware of so no drips out of the T&P valve. I suppose the expansion tank would just act like a giant water hammer arrestor, sounds like a good idea - thanks!
 
ludi
Lord High Gerbil
Posts: 8646
Joined: Fri Jun 21, 2002 10:47 pm
Location: Sunny Colorado front range

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 1:16 pm

Captain Ned wrote:
XorCist wrote:
why do u need a hot water temp regulator coming off the water heater? why not just turn down the thermostat on the water heater itself?

Many local plumbing codes call for the heater to be kept above 140F to kill off any nasties that might be in the water. Since 140+ is unsafe at the tap, the code also requires a mixing valve to reduce the output to 120F or lower.

I installed my own water heater so I never bothered with the mixing valve.

As a nice bonus, the hot water supply lasts longer because the effective tank volume is the actual volume multiplied by the average mixing ratio. Also, this is the only correct way to set up a water heater when it it is supplying a recirculating heating system in a small apartment or cabin. I once lived in some school-owned apartment housing that used such systems with water heaters that did not use mixing valves and could not be turned above 120-125F without tripping the TPR. That housing was less than 10 years old at the time, too. I think the architectural engineer should have been forced to spend a winter there as punishment.
Abacus Model 2.5 | Quad-Row FX with 256 Cherry Red Slider Beads | Applewood Frame | Water Cooling by Brita Filtration
 
anotherengineer
Gerbil Jedi
Posts: 1688
Joined: Fri Sep 25, 2009 1:53 pm
Location: Northern, ON Canada, Yes I know, Up in the sticks

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 1:46 pm

As someone else said an expansion tank is usually recommended on the cold side of a hot water tank. A mixing valve like you said is to regulate temperature. Code here in Canada is no hotter than 49C. I would adjust your tank so that your hot water temp is 49C or lower and remove the mixing valve(reducing temp will save some energy costs also)

GSW and john woods (same products) will have some info on piping schematics for HWT's
Life doesn't change after marriage, it changes after children!
 
notfred
Maximum Gerbil
Topic Author
Posts: 4610
Joined: Tue Aug 10, 2004 10:10 am
Location: Ottawa, Canada

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 1:53 pm

As ludi said a mixing valve virtually increases the tank volume, and it also gives most of the energy savings that a lower tank temperature would. It really is the best of all worlds apart from this clunk-chunk noise it makes if a tap is shut too quickly. I'm going to look in to the expansion tank idea.
 
Captain Ned
Global Moderator
Posts: 28704
Joined: Wed Jan 16, 2002 7:00 pm
Location: Vermont, USA

Re: Noisy hot water mixing valve

Wed Aug 15, 2012 2:21 pm

notfred wrote:
As ludi said a mixing valve virtually increases the tank volume, and it also gives most of the energy savings that a lower tank temperature would.

That's why I love my indirect HW heater. Put it in to replace a direct-fired coil in the boiler which, while always hot, could produce about 2 gal/min of hot water. Now I've got a big 50 gallon tank that gets its heat from a loop run off the boiler (essentially a third zone in my HW heating system). Haven't run out of hot water since.
What we have today is way too much pluribus and not enough unum.